参数表节选:的技术参数 KFD2-SR2-Ex2.W
General specifications | ||
Signal type | Digital Input | |
Functional safety related parameters | ||
Safety Integrity Level (SIL) | SIL 2 | |
Supply | ||
Connection | Power Rail or terminals 14+, 15- | |
Rated voltage | 19 ... 30 V DC | |
Ripple | ≤ 10 % | |
Rated current | ≤ 50 mA | |
Power dissipation | ≤ 1 W | |
Power consumption | ≤ 1 W | |
Input | ||
Connection side | field side | |
Connection | terminals 1+, 2+, 3-; 4+, 5+, 6- | |
Rated values | acc. to EN 60947-5-6 (NAMUR) | |
Open circuit voltage/short-circuit current | approx. 8 V DC / approx. 8 mA | |
Switching point/switching hysteresis | 1.2 ... 2.1 mA / approx. 0.2 mA | |
Line fault detection | breakage I ≤ 0.1 mA , short-circuit I > 6 mA | |
Pulse/Pause ratio | min. 20 ms / min. 20 ms | |
Output | ||
Connection side | control side | |
Connection | output I: terminals 7, 8, 9 ; output II: terminals 10, 11, 12 | |
Output I, II | signal, relay | |
Contact loading | 250 V AC/2 A/cos φ > 0.75; 126.5 V AC/4 A/cos φ > 0.75; 40 V DC/2 A resistive load | |
Minimum switch current | 2 mA / 24 V DC | |
Energized/De-energized delay | approx. 20 ms / approx. 20 ms | |
Mechanical life | 107 switching cycles | |
Collective error message | Power Rail | |
Transfer characteristics | ||
Switching frequency | ≤ 10 Hz | |
Galvanic isolation | ||
Input/Output | reinforced insulation according to IEC/EN 61010-1, rated insulation voltage 300 Veff | |
Input/power supply | reinforced insulation according to IEC/EN 61010-1, rated insulation voltage 300 Veff | |
Output/power supply | reinforced insulation according to IEC/EN 61010-1, rated insulation voltage 300 Veff | |
Output/Output | reinforced insulation according to IEC/EN 61010-1, rated insulation voltage 300 Veff | |
Indicators/settings | ||
Display elements | LEDs | |
Control elements | DIP switch | |
Configuration | via DIP switches | |
Labeling | space for labeling at the front |